Tripplite Output Current create own graphs

Has anyone been monitoring Tripplite Devices and realized that the Output Current is reported as .05 vs .5 Amps. It happens on both UPS and PDU devices.
I walk the devices with the current OID libreNMS is. The value comes back as 5 but in the database it shows .5 so when it’s being graphed still shows .5. Also the Min and max values are reported the same.

Is there a way to change the Temp of the battery to Fahrenheit instead of Celsius?

I noticed not much was collected from Tripplites. Is there a way to insert my own OIDs and have them Graph?

We have to put some customisation in because they suck at following mibs.

Please post the output of ./discovery.php -h HOSTNAME -d

Hey thank you,
Here is the Data Base output, discovery.php and pics

select * from sensors where device_id = ‘995’;
8830 | 0 | current | 995 | snmp | .1.3.6.1.2.1.33.1.4.4.1.3.1 | 1 | rfc1628 | Output | 10 | 1 | 0.6 | 1.05 | NULL | NULL | NULL | 1 | No | NULL | NULL | 2017-05-18 08:12:56 | 0.6 |

./discovery.php -h 172.30.15.98 -d
LibreNMS Discovery
===================================
Version info:
Commit SHA: a475069c9bc768857876e4ec5c4aee0176690af5
Commit Date: 1493858725
DB Schema: 189
PHP: 7.0.18
MySQL: 5.5.52-MariaDB
RRDTool: 1.4.8
SNMP: NET-SNMP 5.7.2
==================================DEBUG!
DB Schema update started…
SQL[SELECT version FROM dbSchema ORDER BY version DESC LIMIT 1]
DB Schema already up to date.
SQL[SELECT * FROM devices WHERE status = 1 AND disabled = 0 AND hostname LIKE ‘172.30.15.98’ ORDER BY device_id DESC]
SQL[SELECT * FROM devices_attribs WHERE device_id = ‘995’]
172.30.15.98 995 poweralert SQL[INSERT INTO device_perf (xmt,rcv,loss,min,max,avg,device_id,timestamp) VALUES (‘3’,‘3’,‘0’,‘0.91’,‘1.49’,‘1.29’,‘995’,NOW())]
SNMP Check response code: 0

Modules status: Global+ OS+ Device
#### Load disco module os ####
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Ovq -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 SNMPv2-MIB::sysDescr.0]
POWERALERT 12
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Ovqn -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 SNMPv2-MIB::sysObjectID.0]
.*.4.1.850.1
| POWERALERT 12 | .1.3.6.1.4.1.850.1 |
>> Runtime for discovery module 'os': 0.1280 seconds with 888 bytes
#### Unload disco module os ####
Modules status: Global+ OS+ Device
#### Load disco module ports ####
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m IF-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 ifDescr]
ifDescr.1 = eth0
ifDescr.2 = LOOPBACK
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m IF-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 ifName]
ifName = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m IF-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 ifAlias]
ifAlias = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m IF-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 ifType]
ifType.1 = softwareLoopback
ifType.2 = ethernetCsmacd
Array
(
    [1] => Array
        (
            [ifDescr] => eth0
            [ifType] => softwareLoopback
        )
    [2] => Array
        (
            [ifDescr] => LOOPBACK
            [ifType] => ethernetCsmacd
        )
)
SQL[SELECT `name` FROM `port_association_mode` WHERE pom_id = '1']
SQL[SELECT * FROM `ports` WHERE `device_id` = '995' ORDER BY port_id]
..
>> Runtime for discovery module 'ports': 1.9070 seconds with 2056 bytes
#### Unload disco module ports ####
Modules status: Global+ OS- Device  Module [ ports-stack ] disabled on os.
Modules status: Global+ OS- Device  Module [ entity-physical ] disabled on os.
Modules status: Global+ OS+ Device
#### Load disco module processors ####
 hrDevice: SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m HOST-RESOURCES-MIB:HOST-RESOURCES-TYPES -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 hrDevice]
hrDevice = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m HOST-RESOURCES-MIB:HOST-RESOURCES-TYPES -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 hrProcessorLoad]
hrProcessorLoad = No Such Object available on this agent at this OID
SQL[SELECT COUNT(*) FROM `processors` WHERE `device_id` = '995' AND `processor_type` != 'ucd-old']
SQL[SELECT * FROM `processors` WHERE `device_id`  = '995']
>> Runtime for discovery module 'processors': 1.8530 seconds with 34936 bytes
#### Unload disco module processors ####
Modules status: Global+ OS+ Device
#### Load disco module mempools ####
SQL[SELECT COUNT(*) FROM `mempools` WHERE `device_id` = '995' AND `mempool_type` = 'cemp']
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m NETSWITCH-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert:/opt/librenms/mibs/hp udp:HOSTNAME:161 hpLocal]
hpLocalMem = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m NETSWITCH-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert:/opt/librenms/mibs/hp udp:HOSTNAME:161 hpGlobal]
hpGlobalMem = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m HOST-RESOURCES-MIB:HOST-RESOURCES-TYPES:NetWare-Host-Ext-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 hrStorageEntry]
hrStorageEntry = No Such Object available on this agent at this OID
SQL[SELECT * FROM `mempools` WHERE `device_id`  = '995']
>> Runtime for discovery module 'mempools': 1.2210 seconds with 23112 bytes
#### Unload disco module mempools ####
Modules status: Global+ OS- Device  Module [ cisco-vrf-lite ] disabled on os.
Modules status: Global- OS- Device  Module [ cisco-mac-accounting ] disabled on os.
Modules status: Global- OS- Device  Module [ cisco-pw ] disabled on os.
Modules status: Global- OS- Device  Module [ cisco-vrf ] disabled on os.
Modules status: Global- OS  Device  Module [ cisco-cef ] disabled globally.
Modules status: Global- OS- Device  Module [ cisco-sla ] disabled on os.
Modules status: Global- OS  Device  Module [ cisco-cbqos ] disabled globally.
Modules status: Global- OS  Device  Module [ cisco-otv ] disabled globally.
Modules status: Global+ OS+ Device
#### Load disco module ipv4-addresses ####
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -Osq -m IP-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 ipAdEntIfIndex]
ipAdEntIfIndex.* 1
ipAdEntIfIndex.* 2
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -m IP-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 ipAdEntNetMask.127.0.0.1]
*
SQL[SELECT COUNT(*) FROM `ports` WHERE device_id = '995' AND `ifIndex` = '1']
SQL[SELECT `port_id` FROM `ports` WHERE `device_id` = '995' AND `ifIndex` = '1']
SQL[SELECT COUNT(*) FROM `ipv4_networks` WHERE `ipv4_network` = '127.0.0.1/32']
SQL[UPDATE `ipv4_networks` set `context_name` ='' WHERE `ipv4_network` = '127.0.0.1/32']
sSQL[SELECT `ipv4_network_id` FROM `ipv4_networks` WHERE `ipv4_network` = '127.0.0.1/32']
SQL[SELECT COUNT(*) FROM `ipv4_addresses` WHERE `ipv4_address` = '127.0.0.1' AND `ipv4_prefixlen` = '32' AND `port_id` = '28844' ]
SQL[UPDATE `ipv4_addresses` set `context_name` ='' WHERE `ipv4_address` = '127.0.0.1' AND `ipv4_prefixlen` = '32' AND `port_id` = '28844']
.SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -m IP-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 ipAdEntNetMask.172.30.15.98]
*
SQL[SELECT COUNT(*) FROM `ports` WHERE device_id = '995' AND `ifIndex` = '2']
SQL[SELECT `port_id` FROM `ports` WHERE `device_id` = '995' AND `ifIndex` = '2']
SQL[SELECT COUNT(*) FROM `ipv4_networks` WHERE `ipv4_network` = '172.30.15.96/28']
SQL[UPDATE `ipv4_networks` set `context_name` ='' WHERE `ipv4_network` = '172.30.15.96/28']
sSQL[SELECT `ipv4_network_id` FROM `ipv4_networks` WHERE `ipv4_network` = '172.30.15.96/28']
SQL[SELECT COUNT(*) FROM `ipv4_addresses` WHERE `ipv4_address` = '172.30.15.98' AND `ipv4_prefixlen` = '28' AND `port_id` = '28845' ]
SQL[UPDATE `ipv4_addresses` set `context_name` ='' WHERE `ipv4_address` = '172.30.15.98' AND `ipv4_prefixlen` = '28' AND `port_id` = '28845']
.SQL[SELECT `ipv4_addresses`.*, `ports`.`device_id`, `ports`.`ifIndex` FROM `ipv4_addresses` LEFT JOIN `ports` ON `ipv4_addresses`.`port_id` = `ports`.`port_id` WHERE `ports`.device_id = '995' OR `ports`.`device_id` IS NULL]
>> Runtime for discovery module 'ipv4-addresses': 0.0880 seconds with 4664 bytes
#### Unload disco module ipv4-addresses ####
Modules status: Global+ OS- Device  Module [ ipv6-addresses ] disabled on os.
Modules status: Global- OS- Device  Module [ route ] disabled on os.
Modules status: Global+ OS+ Device
#### Load disco module sensors ####
Pre-cache poweralert: tlUpsSnmpCardSerialNum SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Ovq -m TRIPPLITE-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.4.1.850.100.1.1.4.0]
Expected IDENTIFIER (_): At line 355 in /opt/librenms/mibs/poweralert/TRIPPLITE-MIB
"2550AV0AC899001645"
Array
(
    [poweralert_serial] => 2550AV0AC899001645
)
 ENTITY-SENSOR: Caching OIDs: entPhysicalDescrSNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m CISCO-ENTITY-SENSOR-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 entPhysicalDescr]
entPhysicalDescr = No Such Object available on this agent at this OID
 entPhysicalNameSNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m CISCO-ENTITY-SENSOR-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 entPhysicalName]
entPhysicalName = No Such Object available on this agent at this OID
 entPhySensorTypeSNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m ENTITY-SENSOR-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 entPhySensorType]
entPhySensorType = No Such Object available on this agent at this OID
 entPhySensorScaleSNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m ENTITY-SENSOR-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 entPhySensorScale]
entPhySensorScale = No Such Object available on this agent at this OID
 entPhySensorPrecisionSNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m ENTITY-SENSOR-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 entPhySensorPrecision]
entPhySensorPrecision = No Such Object available on this agent at this OID
 entPhySensorValueSNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m ENTITY-SENSOR-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 entPhySensorValue]
entPhySensorValue = No Such Object available on this agent at this OID
SQL[SELECT attrib_value FROM devices_attribs WHERE `device_id` = '995' AND `attrib_type` = 'ipmi_hostname' ]
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='voltage' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'ipmi']
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='temperature' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'ipmi']
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='fanspeed' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'ipmi']
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='power' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'ipmi']
Airflow: SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='airflow' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
Current: RFC1628 SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -Osqn -m UPS-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.6]
.*.*.2.6 No Such Instance currently exists at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.3.0]
.*.*.4.3.0 1
.1.3.6.1.2.1.33.1.4.3.0 1
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.4.1.3.1]
6
Discover sensor: .1.3.6.1.2.1.33.1.4.4.1.3.1, 1, rfc1628, Output, snmp, 10, 1, , 0.6
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'current' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '1']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'current' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '1']
.SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.3.2.0]
.*.*.3.2.0 1
.1.3.6.1.2.1.33.1.3.2.0 1
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.3.3.1.4.1]
No Such Instance currently exists at this OID
Discover sensor: .1.3.6.1.2.1.33.1.3.3.1.4.1, 101, rfc1628, Input, snmp, 10, 1, , 0
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'current' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '101']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'current' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '101']
.SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.5.2.0]
.*.*.5.2.0 No Such Instance currently exists at this OID
Array
(
    [rfc1628] => Array
        (
            [1] => 1
            [101] => 1
        )
)
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='current' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
1 -> rfc1628
101 -> rfc1628
Charge: RFC1628 SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -Osqn -m UPS-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.4]
.*.*.2.4.0 100 percent
.1.3.6.1.2.1.33.1.2.4.0 100 percent
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -O vq -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.4.0]
100
Discover sensor: .1.3.6.1.2.1.33.1.2.4.0, 500, rfc1628, Battery charge remaining, snmp, 1, 1, , 100
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'charge' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '500']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'charge' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '500']
.Array
(
    [rfc1628] => Array
        (
            [500] => 1
        )
)
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='charge' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
500 -> rfc1628
Dbm: SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='dbm' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
Fanspeed: SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='fanspeed' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
Frequency: RFC1628 SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.3.2.0]
.*.*.3.2.0 1
.1.3.6.1.2.1.33.1.3.2.0 1
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.3.3.1.2.1]
598
Discover sensor: .1.3.6.1.2.1.33.1.3.3.1.2.1, 3.2.0.1, rfc1628, Input, snmp, 10, 1, , 59.8
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'frequency' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '3.2.0.1']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'frequency' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '3.2.0.1']
.SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.2.0]
598
Discover sensor: .1.3.6.1.2.1.33.1.4.2.0, 4.2.0, rfc1628, Output, snmp, 10, 1, , 59.8
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'frequency' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '4.2.0']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'frequency' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '4.2.0']
.SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.5.1.0]
No Such Instance currently exists at this OID
Array
(
    [rfc1628] => Array
        (
            [3.2.0.1] => 1
            [4.2.0] => 1
        )
)
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='frequency' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
3.2.0.1 -> rfc1628
4.2.0 -> rfc1628
Humidity: SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='humidity' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
Load: RFC1628 SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -Osqn -m UPS-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.4.1.5]
.*.*.*.1 37 percent
.1.3.6.1.2.1.33.1.4.4.1.5.1 37 percent
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -O vq -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.4.1.5.1]
37
Discover sensor: .1.3.6.1.2.1.33.1.4.4.1.5.1, 501, rfc1628, Percentage load, snmp, 1, 1, , 37
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'load' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '501']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'load' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '501']
.Array
(
    [rfc1628] => Array
        (
            [501] => 1
        )
)
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='load' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
501 -> rfc1628
Power: RFC1628 SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.3.0]
.*.*.4.3.0 1
.1.3.6.1.2.1.33.1.4.3.0 1
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.4.1.4.1]
712
Discover sensor: .1.3.6.1.2.1.33.1.4.4.1.4.1, 301, rfc1628, Output, snmp, 1, 1, , 712
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'power' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '301']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'power' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '301']
.SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.3.2.0]
.*.*.3.2.0 1
.1.3.6.1.2.1.33.1.3.2.0 1
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.3.3.1.5.1]
No Such Instance currently exists at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.5.2.0]
.*.*.5.2.0 No Such Instance currently exists at this OID
Array
(
    [rfc1628] => Array
        (
            [301] => 1
        )
)
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='power' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
301 -> rfc1628
Runtime: RFC1628 SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.2.0]
No Such Instance currently exists at this OID
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Ovq -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.3.0]
15
Discover sensor: .1.3.6.1.2.1.33.1.2.3.0, 200, rfc1628, Estimated battery time remaining, snmp, 1, 1, , 15
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'runtime' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '200']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'runtime' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '200']
.Array
(
    [rfc1628] => Array
        (
            [200] => 1
        )
)

SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='runtime' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
200 -> rfc1628
Signal: SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='signal' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
State: RFC1628 SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Ovqe -m UPS-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 upsBatteryStatus.0]
2
SQL[SELECT `state_index_id` FROM state_indexes WHERE state_name = 'upsBatteryStatusState' LIMIT 1]
SQL[SELECT * FROM `state_translations` WHERE `state_index_id` = '12']
Discover sensor: .1.3.6.1.2.1.33.1.2.1.0, 0, upsBatteryStatusState, Battery Status, snmp, 1, 1, 0, 2
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'state' AND `device_id` = '995' AND sensor_type = 'upsBatteryStatusState' AND `sensor_index` = '0']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'state' AND `device_id` = '995' AND `sensor_type` = 'upsBatteryStatusState' AND `sensor_index` = '0']
.SQL[SELECT sensor_id FROM `sensors` WHERE `sensor_class` = 'state' AND `device_id` = '995' AND `sensor_type` = 'upsBatteryStatusState' AND `sensor_index` = '0']
SQL[SELECT state_index_id FROM `state_indexes` WHERE `state_name` = 'upsBatteryStatusState']
SQL[INSERT INTO `sensors_to_state_indexes` (`sensor_id`,`state_index_id`)  VALUES ('8865','12')]
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Ovqe -m UPS-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 upsOutputSource.0]
3
SQL[SELECT `state_index_id` FROM state_indexes WHERE state_name = 'upsOutputSourceState' LIMIT 1]
SQL[SELECT * FROM `state_translations` WHERE `state_index_id` = '13']
Discover sensor: .1.3.6.1.2.1.33.1.4.1.0, 0, upsOutputSourceState, Output Source, snmp, 1, 1, 0, 3
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'state' AND `device_id` = '995' AND sensor_type = 'upsOutputSourceState' AND `sensor_index` = '0']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'state' AND `device_id` = '995' AND `sensor_type` = 'upsOutputSourceState' AND `sensor_index` = '0']
.SQL[SELECT sensor_id FROM `sensors` WHERE `sensor_class` = 'state' AND `device_id` = '995' AND `sensor_type` = 'upsOutputSourceState' AND `sensor_index` = '0']
SQL[SELECT state_index_id FROM `state_indexes` WHERE `state_name` = 'upsOutputSourceState']
SQL[INSERT INTO `sensors_to_state_indexes` (`sensor_id`,`state_index_id`)  VALUES ('8866','13')]
Array
(
    [upsBatteryStatusState] => Array
        (
            [0] => 1
        )
    [upsOutputSourceState] => Array
        (
            [0] => 1
        )
)
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='state' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
0 -> upsBatteryStatusState
0 -> upsOutputSourceState
Temperature: SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -Osqn -m UPS-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.7]
.*.*.2.7.0 35 degrees Centigrade
.1.3.6.1.2.1.33.1.2.7.0 35 degrees Centigrade
RFC1628 Battery Temperature SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Ovq -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.7.0]
35
Discover sensor: .1.3.6.1.2.1.33.1.2.7.0, 0, rfc1628, Battery, snmp, 1, 1, , 35
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'temperature' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '0']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'temperature' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '0']
.Array
(
    [rfc1628] => Array
        (
            [0] => 1
        )
)
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='temperature' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
0 -> rfc1628
Voltage: RFC1628 SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -Osqn -m UPS-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.5]
.*.*.2.5.0 546 0.1 Volt DC
.1.3.6.1.2.1.33.1.2.5.0 546 0.1 Volt DC
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -O vq -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.2.5.0]
546
Discover sensor: .1.3.6.1.2.1.33.1.2.5.0, 1.2.5.0, rfc1628, Battery, snmp, 1, 1, , 546
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'voltage' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '1.2.5.0']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'voltage' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '1.2.5.0']
.SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.3.0]
.*.*.4.3.0 1
.1.3.6.1.2.1.33.1.4.3.0 1
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.4.4.1.2.1]
116
Discover sensor: .1.3.6.1.2.1.33.1.4.4.1.2.1, 1, rfc1628, Output, snmp, 1, 1, , 116
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'voltage' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '1']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'voltage' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '1']
.SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.3.2.0]
.*.*.3.2.0 1
.1.3.6.1.2.1.33.1.3.2.0 1
SNMP[/usr/bin/snmpget -v2c -c COMMUNITY -Oqv -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.3.3.1.3.1]
116
Discover sensor: .1.3.6.1.2.1.33.1.3.3.1.3.1, 101, rfc1628, Input, snmp, 1, 1, , 116
SQL[SELECT COUNT(sensor_id) FROM `sensors` WHERE `poller_type`= 'snmp' AND `sensor_class` = 'voltage' AND `device_id` = '995' AND sensor_type = 'rfc1628' AND `sensor_index` = '101']
SQL[SELECT * FROM `sensors` WHERE `sensor_class` = 'voltage' AND `device_id` = '995' AND `sensor_type` = 'rfc1628' AND `sensor_index` = '101']
.SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OsqnU -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 .1.3.6.1.2.1.33.1.5.2.0]
.*.*.5.2.0 No Such Instance currently exists at this OID
Array
(
    [rfc1628] => Array
        (
            [1.2.5.0] => 1
            [1] => 1
            [101] => 1
        )
)
SQL[SELECT * FROM sensors AS S, devices AS D WHERE S.sensor_class='voltage' AND S.device_id = D.device_id AND D.device_id = '995' AND S.poller_type = 'snmp']
1.2.5.0 -> rfc1628
1 -> rfc1628
101 -> rfc1628
>> Runtime for discovery module 'sensors': 38.1500 seconds with 19896 bytes
#### Unload disco module sensors ####
Modules status: Global+ OS+ Device
#### Load disco module storage ####
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m EQLVOLUME-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert:/opt/librenms/mibs/equallogic udp:HOSTNAME:161 EqliscsiVolumeEntry]
eqliscsiVolumeEntry = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m HOST-RESOURCES-MIB:HOST-RESOURCES-TYPES:NetWare-Host-Ext-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 hrStorageEntry]
hrStorageEntry = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m NETAPP-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 dfEntry]
dfEntry = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m UCD-SNMP-MIB -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 dskTable]
dskTable = No Such Object available on this agent at this OID
SQL[SELECT `storage_descr` FROM `storage` WHERE `device_id`  = '995' AND `storage_type` != 'dsk']
SQL[SELECT * FROM `storage` WHERE `device_id`  = '995']
>> Runtime for discovery module 'storage': 3.0210 seconds with 3232 bytes
#### Unload disco module storage ####
Modules status: Global+ OS+ Device
#### Load disco module hr-device ####
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m HOST-RESOURCES-MIB:HOST-RESOURCES-TYPES -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 hrDeviceEntry]
hrDeviceEntry = No Such Object available on this agent at this OID
SNMP[/usr/bin/snmpbulkwalk -v2c -c COMMUNITY -OQUs -m HOST-RESOURCES-MIB:HOST-RESOURCES-TYPES -M /opt/librenms/mibs:/opt/librenms/mibs/poweralert udp:HOSTNAME:161 hrProcessorEntry]
hrProcessorEntry = No Such Object available on this agent at this OID
Array
(
)
SQL[SELECT * FROM `hrDevice` WHERE `device_id`  = '995']
>> Runtime for discovery module 'hr-device': 1.8530 seconds with 792 bytes
#### Unload disco module hr-device ####
Modules status: Global+ OS- Device  Module [ discovery-protocols ] disabled on os.
Modules status: Global+ OS- Device  Module [ arp-table ] disabled on os.
Modules status: Global- OS- Device  Module [ discovery-arp ] disabled on os.
Modules status: Global- OS- Device  Module [ junose-atm-vp ] disabled on os.
Modules status: Global+ OS- Device  Module [ bgp-peers ] disabled on os.
Modules status: Global+ OS- Device  Module [ vlans ] disabled on os.
Modules status: Global- OS- Device  Module [ vmware-vminfo ] disabled on os.
Modules status: Global- OS- Device  Module [ libvirt-vminfo ] disabled on os.
Modules status: Global- OS- Device  Module [ toner ] disabled on os.
Modules status: Global+ OS- Device  Module [ ucd-diskio ] disabled on os.
Modules status: Global- OS  Device  Module [ applications ] disabled globally.
Modules status: Global+ OS- Device  Module [ services ] disabled on os.
Modules status: Global+ OS- Device  Module [ stp ] disabled on os.
Modules status: Global+ OS- Device  Module [ ntp ] disabled on os.
Modules status: Global- OS  Device  Module [ loadbalancers ] disabled globally.
Modules status: Global- OS  Device  Module [ mef ] disabled globally.
Modules status: Global+ OS- Device  Module [ wireless ] disabled on os.
SQL[SELECT attrib_value FROM devices_attribs WHERE `device_id` = '995' AND `attrib_type` = 'poll_mib' ]
SQL[UPDATE `devices` set `last_discovered` =NOW(),`last_discovered_timetaken` ='48.75' WHERE `device_id` = '995']
Discovered in 48.75 seconds
SQL[INSERT INTO `perf_times` (`type`,`doing`,`start`,`duration`,`devices`,`poller`)  VALUES ('discover','172.30.15.98','1495131395.5607','48.97','1','DIT-LibreNMS.cchnl.hnl\n')]
./discovery.php 172.30.15.98 2017-05-18 08:17:24 - 1 devices discovered in 48.97 secs
SNMP: Get[23/7.98s] Walk [37/40.11s]
MySQL: Cell[31/0.03s] Row[21/0.02s] Rows[30/0.04s] Column[1/0.00s] Update[5/0.11s] Insert[4/0.45s] Delete[0/0.00s]

Sorry It didnt let me post it all in one message.

Just use pastebin, it’s extremely difficult to read a wall of text in the forum.

https://pastebin.com/dW48Xguq

Hi @laf were you ever able to find a fix? Thank You

So a new HTML 5 Tripplite SNMP card came out a few months ago. OID values seem to work fine except for PDU. When installing into a UPS sensor values report but when in a PDU no values are reported. The Values are the same for both PDU and UPS? anyway to have it walk for those values on a PDU?